! t, g1 Z& |+ u9 {& B" C( MTwo cutler –hammer advantage starters are doing the same thing:2 i1 v% e. a; s7 b
After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again.
. D/ M7 ]0 n2 Y& AIt is a cycle.
# ~& o8 e8 n! r0 w$ ?" {5 S# R7 Z# |* O" I( l* w
We isolate the network control and use the local start and stop only, the problem remains.
* Y5 ~% h- |) v0 w8 L3 q& LSwap one of the defective buckets with a good one, the new bucket works fine.
: o( k4 t: m/ K6 m8 ?! o' ^The problem should be inside the bucket.5 P+ N! w# @, T/ |' h
& i. j( B5 u- U4 s5 ?9 G" ]1 }
When the problem happened, we observed that the contactor has a pulling action but will not seal.% T3 M% C. L% D, J w
Use a terminating screw divers to push in the contactor, it will not seal either.8 f$ M" m+ F! c, _% d6 k8 Z* Y
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.$ o7 q/ ^ J7 m x+ ~! ?
' h. C" K2 F/ T1 w1 p/ LThe next thing we can think of is the coil, we took the coil out to have a close look.
) y6 J( ?9 Q7 {* ~" JThey have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.4 N$ J5 B& N/ D: [0 `/ [- x
It is getting better this time, we have 7-8 times of running before it quit working. " W- a1 X% q" u3 n. o, ~
, j; \3 ?; [1 r1 m# kThe coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. , l8 J0 V! z6 C
7 m. g0 D& B8 h! n* R% ~Do you guys have any input on this issue? |
|